I'am considering this unit and was wondering how constant a voltage this unit is able to maintain. I know that there are three digital meters on the front. One shows actual line voltage delivered to the unit from the wall, another the voltage the unit is delivering to the system, and a third the difference between the other two. I would like to know how close to 120 volts the unit is able to maintain in actual use. If you have this unit dose the digital read out always stay a constant 120 volts or does it vary by a tenth of a volt or more on the meter? Thanks in advance Gary
mystang

Showing 1 response by liketolisten

Hi, My avs2000 fluctuates +/- 2 to 3 tenths of a volt on the output when the line voltage fluctuates -8 to +3 volts. The noises the unit makes are the servo switches changing taps on the transformer to stabilize the output voltage. The third display on mine is an amp-meter to show current draw of the connected load. I felt the avs200 made a noticeable difference in my system. Hope this helps.

Best Regards,

Greg.