15A or 20A wall recepticles?


Which is best suited for 20amp breaker. This is for monoblock amps.
kenbo

Showing 2 responses by sufentanil

If you have only one outlet on the circuit, it must be a 20A outlet. For multiple outlets, it is permissable to use 15A outlets, but I generally use 20A outlets. If you have the capability, might as well advertise it, right? And I'm sure you're already aware that you need to use 12 ga wire.

Good luck.

Michael
No, Sfar, it is NOT required to use a 20A receptacle on a branch circuit rated at 20A UNLESS the receptacle is the ONLY one on the circuit. Why don't you test this in your own house: Kitchens required 2 20A circuits (GFCI-protected), and bathrooms require a 20A circuit (GFCI-protected). Go down and look at your electrical panel. If your wiring is reasonably recent, you will see 20A breakers for both and 12ga wire coming out. Now look at the outlets themselves. I'm willing to bet that at least some are 15A GFCI (or GFCI-protected by breaker or upstream GFCI outlet).

And to my buddy Steve, it's been a while. We'll catch up soon.

I hope that clarifies things, Kenbo.

Michael