Ngjockey,
I've been abusing the FedEx guys for some time now. I think its only fair I spread the love.
David,
60dB is what the fan on my computer case generates from an inch away, which is fairly unobtrusive. But as you suggested I did set a boombox at the same level from a meter away and shut the furnace room door. It was quite audible--possibly my hearing is better at these frequencies. And then the burner on the water heater kicked in. I will definitely be putting some sort of sound insulation on that room, transformer or not.
Jim,
Thanks greatly for all of that. You've clarified a number of items. But there are a few things I'm not sure about yet. If I understand you correctly there will be three wires running from the secondary winding to the isolated main panel. One leg will be the hot at 120V to feed the breakers. The second (center-tap?) will go to the neutral bar. The third at the other end of the winding will be attached to ground on the panel. And this will necessarily put all circuits in the isolated panel on the same phase. And the neutral bar, ground bar, and panel will all be connected and grounded back at the main service ground. Is this correct?
And if my math is right, a 7.5kva transformer would accomodate a load of 62.5 amps@120V, just enough for four 15 amp circuits. And I would need a 10kva transformer to accomodate a load of 83.3 amps@120V, enough for four 20 amp circuits. Is there any wiggle room here?
You raised the issue of cost. Is having a transformer hooked up 24/7 like leaving my electric range on all the time? Well probably not that expensive. But 10kw x 24hours x 365days x 8.38cents/kwh=$7,340.88 per year to keep it hooked up. Is this the way it works? That would be prohibitive.
As far as whether I need a transformer in the first place, I honestly don't know. How would I know whether my power is dirty? I thought that perhaps I should also be concerned with noise in my ciruits from everything else on my service. I've got fluorescent lights, dimmer switches, computers, a plasma, etc.
I've got a 200amp service to the house and three unused spaces on the panel. Could you please clarify your last comment regarding overkilling the feeder wire size--the feeder going to the subpanel?
Chris
I've been abusing the FedEx guys for some time now. I think its only fair I spread the love.
David,
60dB is what the fan on my computer case generates from an inch away, which is fairly unobtrusive. But as you suggested I did set a boombox at the same level from a meter away and shut the furnace room door. It was quite audible--possibly my hearing is better at these frequencies. And then the burner on the water heater kicked in. I will definitely be putting some sort of sound insulation on that room, transformer or not.
Jim,
Thanks greatly for all of that. You've clarified a number of items. But there are a few things I'm not sure about yet. If I understand you correctly there will be three wires running from the secondary winding to the isolated main panel. One leg will be the hot at 120V to feed the breakers. The second (center-tap?) will go to the neutral bar. The third at the other end of the winding will be attached to ground on the panel. And this will necessarily put all circuits in the isolated panel on the same phase. And the neutral bar, ground bar, and panel will all be connected and grounded back at the main service ground. Is this correct?
And if my math is right, a 7.5kva transformer would accomodate a load of 62.5 amps@120V, just enough for four 15 amp circuits. And I would need a 10kva transformer to accomodate a load of 83.3 amps@120V, enough for four 20 amp circuits. Is there any wiggle room here?
You raised the issue of cost. Is having a transformer hooked up 24/7 like leaving my electric range on all the time? Well probably not that expensive. But 10kw x 24hours x 365days x 8.38cents/kwh=$7,340.88 per year to keep it hooked up. Is this the way it works? That would be prohibitive.
As far as whether I need a transformer in the first place, I honestly don't know. How would I know whether my power is dirty? I thought that perhaps I should also be concerned with noise in my ciruits from everything else on my service. I've got fluorescent lights, dimmer switches, computers, a plasma, etc.
I've got a 200amp service to the house and three unused spaces on the panel. Could you please clarify your last comment regarding overkilling the feeder wire size--the feeder going to the subpanel?
Chris