I'm trying to get a handle on exactly what to ask of my electrician. I've been searching past threads for awhile now and I might know just enough to ask questions. I'm going to need power for the usual array of AV toys: monos, a pre-amp, CDP, TT, tuner, and plasma TV, BluRay, etc., and I hope to do things right. I plan to install a 5kva transformer and a subpanel for six dedicated lines as well as whole house surge suppression and a isolated ground.

1) Which is more desirable--to pull a 240V feeder from the service before it goes to the main panel or from a double breaker at the main panel? If I use the double breaker, does it make a difference where it is located within the main panel?

2) Should I use the isolation transformer to stepdown to 120V or should I take 240V to the sub?

3) Which audio/video components need to be on the same phase?

4) I've only seen diagrams on wiring a main service panel. What is the sub going to look like if I stepdown to 120V? Will it involve taking only one hot leg off the transformer secondary with a center-tap neutral, resulting in something that looks like one side of the main panel? I would think that this would put everything in the sub on the same phase. Correct? Is this the way to go?

5) Anything else I should be mindful of?

I greatly appreciate the help.
iabirder
Ngjockey,

Thanks for the reply. Yeah, I'm confused and probably don't know what I'm doing. But I promise I won't begin installing until I figure it out. Safety IS first. I won't be doing any of this myself, and expect my electrician to follow code.

I really thought a 5kva xfmr would be large enough. I recall a thread where Zargon had a 4kva iso before a sub with six dedicated lines. Though I do recall that Lak had two 5kva isos before a sub, but that was to feed three different sound systems. My equipment isn't crazy big: ARC REF210s, a REF 3, and the plasma tv will draw 328 watts.

Regarding the "isolated ground"--I was going to have all the neutrals and ground wires in the dedicated lines run all the way back to the main service grounding point, per suggestion of Gs5556 in another's thread--although I don't know what this does for my sound, since they all hook together at some point.

I've collected a good bit of possible mis-information regarding grounds, and maybe you can help me sort it out: 1)I've heard of using a separate ground rod that is 6 feet from the service ground. 2)I've heard of using a separate ground rod, but bonding it to the service ground rod. 3)I've heard that the iso xfmr is a separate power supply, thus I can ground everything from the subpanel to the nearby water pipe in the utility room. 4)I've heard that isolated ground receptacles are not necessary because I have a wood frame house.

So what would be the best way to provide clean power to my gear? Thanks.

Chris

Hi Chris,

I am going through the same process with my AV power.

I have been able to get a great deal of info from not only A-gon threads but also white papers on the Jensen Transformer site (Bill Whitlock, Jensen President, has published a lot of peer-reviewed papers on grounding issues), the Ultra-K white papers from the Controlled Power site, the white papers from the Middle Atlantic Products site, the white papers from the Equi=tech site, white papers from the Ground1 site, and papers from the publications page of the Audio Systems Group site.

There is a difference between Hospital Grade Outlets (greater contact force among other benefits) and outlets with Isolated Grounds. Isolated ground duplexes separate the ground lead from the mounting strap of the duplex -- so the ground wire can be isolated from the building ground (metal boxes in the wall, other outlet grounds, etc) until the isolated ground meets up with the other grounds at the source (main panel or isolation transformer). If you check the Hubbell-Wiring site, you can check their online catalog (Hubbell Wiring Device-Kellems) and will see in section A "straight blade devices" that they make hosptal grade, industrial grade, and commercial spec grade duplexes (and explain the differences); and in section J show isolated ground versions of basic and hospital grade duplexes (plus a good explanation of isolated ground).

I believe the advice you read about isolated grounds not being needed in a wood house is because if you are already running a dedicated line (dedicated hot, neutral, ground) from the panel to your audio gear without making a stop at any other outlet or junction, then the ground is pretty much already isolated because the outlet box is nailed to a wooden stud, not a metal building frame. But I'm not an electrician, nor have I stayed in a Holiday Inn.
Any time it's going to an outlet, instead of hard-wired, you have to accommodate the POTENTIAL, not the actual load. Who's to say you won't get 600W, class A, OTL monoblocks and then plug in some 11,000 BTU portable air conditioners and a vacuum cleaner. Also have to consider the electrical service, since you're adding another 20A without taking anything else away.

The "isolated ground system" has two ground wires, one insulated and going all the way back to the bus bar. Mixed results, mixed recommendations, and not official NEC code. Romex and armored are available as 3C ... but talk about confusing... Got any green nail polish? ;) Otherwise, conduit, $$$.

1) Wrong
2) Ok, maybe, sort of. Ask Almarg.
3) Very wrong. Can't count on copper service pipe. Removed or prohibited from code decades ago. Transformer/shield has to be grounded too.
4) When are they necessary? Google.

Off to a good start. The transformer, though unusual for residential, will provide some common mode noise reduction. Multiple transformers allows isolation between components. Naturally, "the best way" is completely impractical.

Where is this transformer going to be located? They can hum.
DMatt,
Thanks for the info regarding the hospital grade recepticles. I have seen a number of favorite ports mentioned in threads, most often Hubbell 5362s.

Based on what I've gleaned from other threads there is still a benefit to using recepticles with an isolated ground and running the dedicated lines in armored cable. I'm undecided on which to use here. #10 BX has been recommended. I've also seen recommendations for the Belden 8300 series. Also for twisting the wires. Do they need to be twisted if they are running through metal? You'd think someone on Audiogon would have created a cookbook for all this by now.

Ngjockey,
Thanks, I get what you mean by potential draw on the circuits. And I'll simply let the electrician worry about grounding things properly.

You brought up another point though regarding the service amperage that'll go to the sub. I'm trying to get a handle on what's possible. I guess I would like a minimum of four circuits off the subpanel: two for the monos, one analog, and one digital. I've seen recommendations for a minimum 60amp breaker at the main panel to protect what is going to the sub. 1)How do I know what amperage is available to lend the sub? 2)If I can use a 60amp breaker does this mean that I can't exceed a total of 60amps in breakers on the sub?

Chris